Conductor Ampacity
Chapter 12 - Physics Of Conductors And Insulators
PDF Version
The smaller the cross-sectional area of any given wire, the greater the resistance for any given length, all other factors being equal. A wire with greater resistance will dissipate a greater amount of heat energy for any given amount of current, the power being equal to P=I2R.
Dissipated power due to a conductor’s resistance manifests itself in the form of heat, and excessive heat can be damaging to a wire (not to mention objects near the wire), especially considering the fact that most wires are insulated with a plastic or rubber coating, which can melt and burn. Thin wires will, therefore, tolerate less current than thick wires, all other factors being equal. A conductor’s current-carrying limit is known as its ampacity.
Primarily for reasons of safety, certain standards for electrical wiring have been established within the United States, and are specified in the National Electrical Code (NEC). Typical NEC wire ampacity tables will show allowable maximum currents for different sizes and applications of wire. Though the melting point of copper theoretically imposes a limit on wire ampacity, the materials commonly employed for insulating conductors melt at temperatures far below the melting point of copper, and so practical ampacity ratings are based on the thermal limits of the insulation. Voltage dropped as a result of excessive wire resistance is also a factor in sizing conductors for their use in circuits, but this consideration is better assessed through more complex means (which we will cover in this chapter). A table derived from an NEC listing is shown for example:
Copper Conductor Ampacities, in Free Air at 30 Degrees C
Insulation: RUW, T THW, THWN FEP, FEPB
Type: TW RUH THHN, XHHW
Table:
Size Current Rating Current Rating Current Rating
AWG @ 60 degrees C @ 75 degrees C @ 90 degrees C
20 *9 - *12.5
19 *13 - 18
16 *18 - 24
14 25 30 35
12 30 35 40
10 40 50 55
8 60 70 80
6 80 95 105
4 105 125 140
2 140 170 190
1 165 195 220
1/0 195 230 260
2/0 225 265 300
3/0 260 310 350
4/0 300 360 405
* = estimated values; normally, these small wire sizes are not manufactured with these insulation types
Notice the substantial ampacity differences between same-size wires with different types of insulation. This is due, again, to the thermal limits (60°, 75°, 90°) of each type of insulation material.
These ampacity ratings are given for copper conductors in “free air” (maximum typical air circulation), as opposed to wires placed in conduit or wire trays. As you will notice, the table fails to specify ampacities for small wire sizes. This is because the NEC concerns itself primarily with power wiring (large currents, big wires) rather than with wires common to low-current electronic work.
There is meaning in the letter sequences used to identify conductor types, and these letters usually refer to properties of the conductor’s insulating layer(s). Some of these letters symbolize individual properties of the wire while others are simply abbreviations. For example, the letter “T” by itself means “thermoplastic” as an insulation material, as in “TW” or “THHN.” However, the three-letter combination “MTW” is an abbreviation for Machine Tool Wire, a type of wire whose insulation is made to be flexible for use in machines experiencing significant motion or vibration.
Insulation Material
  • C = Cotton
  • FEP = Fluorinated Ethylene Propylene
  • MI = Mineral (magnesium oxide)
  • PFA = Perfluoroalkoxy
  • R = Rubber (sometimes Neoprene)
  • S = Silicone “rubber”
  • SA = Silicone-asbestos
  • T = Thermoplastic
  • TA = Thermoplastic-asbestos
  • TFE = Polytetrafluoroethylene (“Teflon”)
  • X = Cross-linked synthetic polymer
  • Z = Modified ethylene tetrafluoroethylene
Heat Rating
  • H = 75 degrees Celsius
  • HH = 90 degrees Celsius
Outer Covering (“Jacket”)
  • N = Nylon
Special Service Conditions
  • U = Underground
  • W = Wet
  • -2 = 90 degrees Celsius and wet
Therefore, a “THWN” conductor has Thermoplastic insulation, is Heat resistant to 75° Celsius, is rated for Wet conditions, and comes with a Nylon outer jacketing.
Letter codes like these are only used for general-purpose wires such as those used in households and businesses. For high-power applications and/or severe service conditions, the complexity of conductor technology defies classification according to a few letter codes. Overhead power line conductors are typically bare metal, suspended from towers by glass, porcelain, or ceramic mounts known as insulators. Even so, the actual construction of the wire to withstand physical forces both static (dead weight) and dynamic (wind) loading can be complex, with multiple layers and different types of metals wound together to form a single conductor. Large, underground power conductors are sometimes insulated by paper, then enclosed in a steel pipe filled with pressurized nitrogen or oil to prevent water intrusion. Such conductors require support equipment to maintain fluid pressure throughout the pipe.
Other insulating materials find use in small-scale applications. For instance, the small-diameter wire used to make electromagnets (coils producing a magnetic field from the flow of electrons) are often insulated with a thin layer of enamel. The enamel is an excellent insulating material and is very thin, allowing many “turns” of wire to be wound in a small space.
REVIEW:
  • Wire resistance creates heat in operating circuits. This heat is a potential fire ignition hazard.
  • Skinny wires have a lower allowable current (“ampacity”) than fat wires, due to their greater resistance per unit length, and consequently greater heat generation per unit current.
  • The National Electrical Code (NEC) specifies ampacities for power wiring based on allowable insulation temperature and wire application.