An Introduction to Transient Voltage Suppressors (TVS)
An intro to transients and the devices used to suppress them. Learn about the variety of devices used to suppress transients.
Technical Article May 24, 2019 by Nick Davis
This article is an intro to transients and the devices used to suppress them. In it, you'll learn about a variety of devices used to suppress transients, including transient voltage suppressor diodes, metal oxide varistors, PolySwitches, and avalanche diodes.
Transients are temporary spikes or surges in voltage or current that can potentially impact circuits in ways ranging from minor glitches to catastrophic failure. A voltage transient can be anywhere from a few millivolts to thousands of volts, and they can last from nanoseconds to hundreds of milliseconds. Some transients are repetitive, such as those caused by inductive ringing in a motor, while other transients are more sporadic, such as ESD events.
Current transients can be caused, for example, by inrush current. The figure below shows a device being hot-plugged.
Inrush Current Spike/Transient.
The applied voltage is 5V (cyan waveform) while the current—technically known as the "inrush current"— (yellow waveform) surges very high: its measured value is 26.2 Amps with a time duration of 21.6µs. In this instance, the device, itself, is able to withstand the current transient. However, depending on the current-sourcing capabilities of the connected power supply, it may become current-limited and, as a result, may starve the device of current. This can result in an undesired device reset or worse.
Origins of Transients
Transients can be generated from internal or external connections to a circuit. Examples of internally generated transients include:
  • Inductive load switching:
    • relay coils
    • motors
    • solenoid coils
    • transformers
  • Arcing:
    • faulty contacts in breakers, switches, and connectors
    • motors with faulty windings or insulation
    • poor electrical wiring
    • poor grounding
  • IC logic switching:​
    • TTL
    • CMOS
Externally generated transients enter a circuit (or system) by pathways including:
  • Power input lines:
    • lightning strikes
    • inductive switching caused by the turning on of other equipment connected to the same power source
  • Data/signal input and/or output lines:
    • I2C
    • serial communication
    • Ethernet
  • Other attached wires/cables, such as grounds
ESD (electrostatic discharge) is another common form of externally generated voltage transient. ESD events can cause either immediate damage or, arguably even worse, latent damage—sometimes referred to as the "walking wounded." The term walking wounded is used because an ESD damaged component may continue to work normally for hours, days, or even months before a catastrophic failure occurs.
Devices Used to Suppress Transients
There is a multitude of devices that can be used to help suppress voltage transients. Such a device is referred to as a Transient Voltage Suppressor (TVS). A few of the more popular TVS devices are listed below.
Bypass Capacitor
Bypass capacitors—used for suppressing voltage transients—are also referred to as decoupling capacitors. Such capacitors, usually in sets of two or three with values of one or two orders of magnitude between them, are often placed at each power source as well as at each analog component to ensure that power supplies are as stable and noise-free as possible.
Capacitor symbol
Typical values:
  • For logic applications: 0.01 - 0.22µF
  • For power applications: 0.1µF and greater
 Applications:
  • Low-power applications
  • RC snubbers
  • Decoupling of digital logic power rails (for cleaner power)
 Advantages:
  • Low cost
  • Readily available
  • Simple to apply
  • Fast acting
 Disadvantages:
  • Uneven suppression
  • Many may be required: one or two for each individual device
Zener Diodes
A Zener diode is a specially designed diode that has a reduced breakdown voltage called the Zener voltage. These diodes exhibit a controlled breakdown which allows the current to keep the voltage across the Zener diode close to the zener breakdown voltage. As a side note, this characteristic is what makes zener diodes useful for generating reference voltages.
Zener diodes are also often used to protect circuits from overvoltage transients, such as ESD events.
Zener diode symbol
Applications:
  • Diversion/clamping in low-energy circuits
  • Good for high-frequency circuits
  • Good for high-speed data lines
Advantages:
  • Low cost
  • Fast acting
  • Easy to use
  • Readily available
  • Standard ratings
  • Bidirectional
  • Calibrated clamping voltage
  • Usually fail open (as opposed to fail short)
Disadvantages:
  • Limited to low-energy handling
Transient Voltage Suppressor Diodes
Transient voltage suppressor diodes are very popular devices used to instantaneously clamp transient voltages (e.g., ESD events) to safe levels before they can damage a circuit. Although standard diodes and Zener diodes can both be used for transient protection, they are actually designed for rectification and voltage regulation, and, therefore, are not as reliable or robust as transient voltage suppressor diodes.
Transient Voltage Suppressor (TVS) Diode Symbols: Unidirectional (left) and bidirectional (right).
Applications:
  • Diversion/clamping in low-energy circuits and systems
  • Good for moderate-frequency applications
 Advantages:
  • Fast acting
  • Easy to use
  • Readily available
  • Bidirectional or unidirectional
  • Calibrated low clamping voltage
  • Fails short-circuited
Disadvantages:
  • High capacitance limits frequency
  • Low energy handling
  • More expensive than Zener diodes, or MOVs
MOVs (Metal Oxide Varistors)
A metal oxide varistor (MOV) is a bidirectional semiconductor voltage transient suppressor. MOVs behave as voltage-sensitive variable resistors. The voltage at which the device conducts (i.e., switches) is a function of the number of grains between its electrode leads. This value can be varied, during the manufacturing process, to create any desired voltage breakdown threshold.
MOVs (Metal Oxide Varistors) symbol
Applications:
  • Diversion/clamping in most low- to moderate-frequency circuits at all voltage and current levels.
  • Can be used in AC or DC applications.
Advantages:
  • Low cost
  • Fast acting
  • Readily available
  • Easy to use
  • Standard ratings
  • Bidirectional
Disadvantages:
  • Moderate- to high-capacitance limits high-frequency performance.
  • Can only dissipate a relatively small amount of power, and, therefore, are unsuited for applications that demand continuous power dissipation.
Avalanche Diode
Avalanche diodes, like Zener diodes, are designed to break down and conduct very high currents at a specific reverse-bias voltage. This behavior is referred to as the avalanche effect. Similar to Zener diodes, which are somewhat restricted in the maximum breakdown voltage range, avalanche diodes are available with breakdown voltages over 4000 V.
Avalanche diodes are connected in a reverse-biased configuration, i.e., the cathode is connected to the more positive voltage. Thus, during normal conditions the diode has minimal effect on the circuit, but when the voltage across its terminals exceeds the specified threshold, it begins to conduct.
Avalanche diode symbol
Applications:
  • Used to protect circuits against damaging high-voltage transients.
Advantages:
  • Specified with a clamping voltage VBR (breakdown voltage).
  • Specified with a maximum-sized transient that it can handle.
  • The avalanche breakdown event is not destructive—assuming the diode isn't overheated.
Disadvantages:
  • A known side effect is RF noise generation.
PolySwitch
A PolySwitch (also referred to as polyfuse or resettable fuse) is a positive temperature coefficient (PTC) resistor that is constructed from a conductive polymer mixture. During normal operating conditions (i.e., during normal temperature conditions), the conductive elements within the PolySwitch form low-resistance "chains" which allow for the current to flow rather easily. However, when the current flowing through these chains increases to a point where their temperature rises above some critical threshold (a point called the "trip current"), the crystalline structure of the conductive polymer abruptly changes into a stretched out and shapeless state which, as a result, increases the resistance of the PolySwitch, which causes a sudden drop in current flow. Once tripped, the PolySwitch will remain in the tripped state until the the fault is removed and the temperature of the PolySwitch returns to a safe level.
PolySwitch symbol
Applications:
  • Overcurrent protection for speakers, motors, power supplies, and battery packs
  • Where a self-resetting fuse (i.e., a fuse that does not require replacement) is needed
Advantages:
  • Low cost
  • Easy to use
  • Self-resetting
Disadvantages:
  • Requires a cooling-down period to reset
TVS Summary
Although many options and devices exist for transient voltage suppression, different TVS devices are more appropriate for certain types of transients or certain operating conditions. It's wise to first understand your circuit's needs and requirements, and then begin your search for the best TVS solution.
Supporting Information
  • Roman Valls May 25, 2017
    Great post and timing since I had a fried RPi yesterday which I fixed replacing the TVSD that was overheating:
    https://www.raspberrypi.org/forums/viewtopic.php?t=46585&p=370751
    https://www.raspberrypi.org/forums/viewtopic.php?f=28&t=34149
    So here goes my question: Are there affordable TVSD that act like a polyfuses but for voltage?
    I want diodes to protect my devices, but I don’t want them breaking *and* preventing the whole system to work again when the external power supply has been fixed/stabilized.
  • N
    ndavis17 May 30, 2017
    Hello Roman!
    Thanks for reading my article.
    I’m not aware of any resettable transient voltage suppressor diodes (TVSD), although TVSDs do have an operating voltage range. Perhaps you could find a TVSD with a higher/larger maximum operating voltage than that of the current TVSD of which you’re using. As far as one being “affordable,” well that depends… affordable is rather a loose term. I did a quick search on Digikey for “transient voltage suppressor diode” and I see their prices range from >$100 to 2.3 cents—of course this depends on the requirements and quantity that you need.
    With all that said…a few other comments:
    You mentioned that your “TVSD that was overheating”, so it sounds like something else is amok. Perhaps the current TVSD is underrated and you simply need to find a more appropriately-sized one.
    You also mentioned “when the external power supply has been fixed/stabilized”. Given this information perhaps you could find a more stable power supply, or at least add some large capacitors to your voltage rail with the intent of providing holdup power/energy to your device/system when a voltage transient occurs; I’d start with using three caps: a 10uF, a 1uF and a 0.1uF ... and then test, adjust, and test again as needed. I come from the world of SSDs (solid state drives). Any reputable SSD has lots and lots of holdup power/energy to address power failure and/or brownout conditions (i.e., voltage transients).
    If you look at the SSD picture from the link below, all the caps at the top-right are used for power holdup. I count about 40 of them!
    https://www.starwindsoftware.com/blog/wp-content/uploads/2016/06/111.png
    You might also consider employing a voltage supervisor or voltage monitor to take some action when a voltage transient is detected, although this approach is more involved as it may require a separate microprocessor and/or cutting up your PCB to access voltage rails and/or control lines.
    I do hope you find this helpful!
    -Nick
    • Roman Valls August 16, 2017
      Thanks Nick, thanks for the elaborate answer! For more context I accidentally injected 12V into my RaspberryPi's USB power lines and of course this guy went hot: https://www.digikey.com/product-detail/en/avx-corporation/SMAJ5.0CA/478-7058-1-ND/3340366 I ordered a replacement, changed it on the RPI board and all started working again fine, no worries whatsoever. So the short was indeed **just** that TVSD and only that component (D17 reference on the original links I posted on my question). That component is placed right at the USB power input and has a relatively straightforward schematic: https://www.raspberrypi.org/app/uploads/2011/12/psu.png What I want is a device (possibly passive without much intelligence/silicon built in) that heats up and disconnects when such situations occur. That is, a polyfuse-like ("self-healing"?) device but for transient voltages instead of in-rush currents. Really appreciate your input and your power electronics SSD experience, cool domain to be in! :)